Design of strip footing


Recommended Posts

Aslamoalaikum. I am trying to design strip footing for a two storey mosque. I have shared load distribution in the photo. There are two beams in the main hall.

I can't figure out how this load distribution can be used to design strip footing for wall 1 and wall 2.

Can anyone guide me?

Assume net allowable bearing capacity is 0.70 T/sft.

Other assumptions

All masonry walls 13.5" thick & 12'0" high

Slabs: 65+65

Finishes: 50+60 psf

Live: 50+50 psf

 

Please guide.

IMG_20230331_194255.jpg

Link to comment
Share on other sites

Lots of questions...

I cannot tell what the framing for this is.  Are the floors structural concrete? or something else. What is the roof construction?  Is it one way, or two way spanning for the slab?  If slabs, is the span for the upper part in a left-right direction?  Why is the middle panel in the upper part different than the panels at each edge? Wouldn't they all be the same? It looks like the spans are approx 15'; does that mean that you are using a 6" slab or something similar?  I don't know what your numbers 61, 61, and 20 represent. I don't know what your loads 50 + 50psf mean.

Edited by Dik
added questions...
Link to comment
Share on other sites

22 hours ago, Dik said:

Lots of questions...

I cannot tell what the framing for this is.  Are the floors structural concrete? or something else. What is the roof construction?  Is it one way, or two way spanning for the slab?  If slabs, is the span for the upper part in a left-right direction?  Why is the middle panel in the upper part different than the panels at each edge? Wouldn't they all be the same? It looks like the spans are approx 15'; does that mean that you are using a 6" slab or something similar?  I don't know what your numbers 61, 61, and 20 represent. I don't know what your loads 50 + 50psf mean.

Floors/slabs are of RCC.

In main hall, there are two beams which are resting on masonry walls (load bearing walls). In all other rooms, slabs are resting directly on masonry walls (load bearing walls).

In the main hall of size 36'×22' (check dimensions), there are two beams. Portion of slab between two beams is two way and remaining two portions are one way.

No using 5" slab.

Numbers 61, 61, 20 represent magnitude of tributary areas formed using one way & two way load distribution concept.

65+65 means 65psf slab at FF and 65psf slab at Roof. 50+65 means 50psf finishes at FF slab and 65psf at Roof slab. 50+50 means 50psf live load at FF slab and roof slab each.

Edited by M. Asad Warraich
Link to comment
Share on other sites

Just now, M. Asad Warraich said:

You can have a look at this drawing. Green lines are two beams.

IMG_20230405_090125.jpg

Portion between two beams is two way slab (shorter dimension: 15'-0", longer dimension: 22'-0")

In main hall (36'×22'), both slabs at sides of beam is one way (9'-3"×22'-0") i.e. 102+102 tributary areas

Link to comment
Share on other sites

I'm listed as an rookie... but, I have over 50 years of experience.  Some comments...

image.thumb.png.a36530aeb301947001cb106567891a01.png

Edited by Dik
Link to comment
Share on other sites

To design Wall - 1 for two storey building, I adopted this method. Please comment.

LOAD CALCULATION

1- Masonry Walls Load 13.5" Thick 12'-0" High

13.5/12×(12+12)×120/1000=3.24 k/ft

2- Parapet Wall Load

4.5/12×2×120/1000=0.10 k/ft

3- Masonry Walls Load 13.5" Thick under plinth level

13.5/12×(3+3)×120/1000=0.81 k/ft

4- Floor Loads

Both beams will bear load coming from slab and transfer it to their ends resting on walls as point loads. That point load will be divided by the width of the tributary area being born by both beams.

Tributary Area of beams for wall - 1=102/2+109/2+109/2+102/2+56=267

Beam size is 12"×18".

> Slabs Loads=65+65=130 psf

Point load due to slabs' distributed loads=267×130/1000=34.71 kips

Divide by width of tributary area=4+7.5/12+15/12+7.5+15/12+4+7.5/12=19.25 feet

Load per unit length due to self weight of slab=34.71/19.25=1.80 k/ft

> Finishes Loads=50+60=110 psf

Using same procedure

Load per unit length due to floor finishes=1.53 k/ft

> Live Load=50+50=100 psf

Load per unit length due to distributed live loads=1.39 k/ft

> PL due to beam self weight

12×18/144×(22/2+13.5/12)×150/1000=2.73 kips for one beam

For four beams (two at FF slab & two at roof slab)=4×2.73=10.91 kips

Divide by width of tributary area=10.91/19.25=0.57 k/ft

TOTAL LOADS ON WALL PER UNIT LENGTH

• Total unfactored dead load=3.24+0.10+0.81+1.80+1.53+0.57=8.05 k/ft

• Total unfactored live load=1.39 k/ft

FOOTING WIDTH REQUIRED

Wreq=(8.05+1.39) / (0.70×2.2045)=6.11 feet

Edited by M. Asad Warraich
Link to comment
Share on other sites

Thanks for the added information. For personal reasons, I don't want to review your calculations, but it looks like you have things in order...

Link to comment
Share on other sites

6 hours ago, M. Asad Warraich said:

WHY 2 WAY ACTION HERE?

Because dimensions of slab in between two beams is 15'-0"×22'-0".

WHY 1 WAY ACTION HERE?

Because it's a verandah and its dimensions are 33'-6"×10'-0".

Just because the aspect ratio of the slab is greater than 2 or whatever, the flexibility of the beams, as opposed to it being a wall support would tend to cause it to behave as a one way slab. Even your load takedown for the wall, as 2 point loads from the slab indicates the one way action. 

Same with the verandah, it doesn't matter what the use of the slab is, it would tend to distribute some of the load at the ends to the adjacent masonry wall. The aspect ratio is still pretty small.

Edited by Dik
Improve the description
Link to comment
Share on other sites

Thanks for your comments. Actually, my purpose of sharing calculations and this post here was to get experts' opinion on if I am doing the design correctly. Would be really grateful if you can have a look at the calculations. Thanks.

Link to comment
Share on other sites

You don't have to look at all the calculations. Just give your opinion on this part of the calculations.

4 hours ago, M. Asad Warraich said:

4- Floor Loads

Both beams will bear load coming from slab and transfer it to their ends resting on walls as point loads. That point load will be divided by the width of the tributary area being born by both beams.

Tributary Area of beams for wall - 1=102/2+109/2+109/2+102/2+56=267

Beam size is 12"×18".

> Slabs Loads=65+65=130 psf

Point load due to slabs' distributed loads=267×130/1000=34.71 kips

Divide by width of tributary area=4+7.5/12+15/12+7.5+15/12+4+7.5/12=19.25 feet

Load per unit length due to self weight of slab=34.71/19.25=1.80 k/ft

 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       