Circular Column Minimum Bars


Waqar Saleem
 Share

Recommended Posts

  • Moderator

salam everybody http://www.sepakistan.com/public/style_emoticons/#EMO_DIR#/smile.png

what should be the minimum number of bars in a circular column???can we use just one bar at center of column?some said that one bar at center cant be used,minmum six bars should be used.

Link to comment
Share on other sites

rft?why we can't use in center?

A column subjected to bending will have one face in tension and other will be in compression. Central bar will have minimal contribution.

If a column with a single rebar is subjected to compressive or tensile force only, in that case rebar would be effective at center or NA. Consider it same as providing reinforcement at Beam Neutral Axis. its a waste. Universities should teach beam column in undergrad so that such concepts be more clear.

Link to comment
Share on other sites

salam everybody :)

what should be the minimum number of bars in a circular column???can we use just one bar at center of column?some said that one bar at center cant be used,minmum six bars should be used.

reminds me of a question on mid term of masters exam, where a concrete wall had temperature of a -30 on 1 side and +18 on other with an udl on top and reinforcement placed at the center of the wall and the question to find the critical load for that given reinforcement and wall section.. that was pretty cruel !

Link to comment
Share on other sites

  • Moderator

thanx @Rana Waseem it's ok spiral confinement is better than rectangular or circular ties,im of the view that if same reinforcement is used both longitudinal main bars and confinement but x-sections are different circular and rectangular in this case which column will have greater strength???

Link to comment
Share on other sites

if you mean to say that we use different concrete section that is i) rectangular & ii) circular but keep the reinforcement and layout of reinforcement same what would be the effect rite?

it will not matter much at normal scale in a normal building unless you have huge dimensions but anyway, ofcourse circular shape is more desireable due to archtectural reasons and also due to structural issues like

circular cols will not have corner stress concentration

less material as compared to square/rect cols but at the same time same moment of inertia

equal capacity at every rotation of axis no matter from where the loading is coming

Link to comment
Share on other sites

The picture below, is of Olive View Hospital, 1971 San Fernando Earthquake, CA, US San Fernando, California, Earthquake February 1971.

11216-San-Fernando--California--Earthquake-February-1971--Damaged-spir.jpg

Here is another view

11217-San-Fernando--California--Earthquake-February-1971--Damaged-spir.jpg

The spiral column displaced 18" from center and is still in good shape and taking load, where as the rectangular columns with ties behaved as below.

eq-colunms-01.JPG

This difference in behavior is attributed to the greater confinement spirals provide resulting into a better "Poisson ratio" & Improved ductility of the system overall. FYI, this building had a soft story and also had hammering due to RCC Core Wall not separated well enough from adjacent part of building.For your question about rectangular or circular column, I would say Circular are good if required for use in high seismic zones and are provided with spirals instead of circular ties. Circular Columns are aesthetically beautiful too.. :)

Link to comment
Share on other sites

and we are using 4 in th lean under footing in SAFE,also we assign soil support to both lean and slab is it a good practise??

dont model lean as part of foundation. just model your slab and assign it supports.

Link to comment
Share on other sites

lean is not part of concrete foundation modelling...unless you are doing a high fi phd scientific research...( i think)...and in ETABS we provide modifiers to account for cracking in concrete members as told in ACI chapter 10..

Link to comment
Share on other sites

The picture below, is of Olive View Hospital, 1971 San Fernando Earthquake, CA, US San Fernando, California, Earthquake February 1971.

11216-San-Fernando--California--Earthquake-February-1971--Damaged-spir.jpg

Here is another view

11217-San-Fernando--California--Earthquake-February-1971--Damaged-spir.jpg

The spiral column displaced 18" from center and is still in good shape and taking load, where as the rectangular columns with ties behaved as below.

eq-colunms-01.JPG

This difference in behavior is attributed to the greater confinement spirals provide resulting into a better "Poisson ratio" & Improved ductility of the system overall. FYI, this building had a soft story and also had hammering due to RCC Core Wall not separated well enough from adjacent part of building.For your question about rectangular or circular column, I would say Circular are good if required for use in high seismic zones and are provided with spirals instead of circular ties. Circular Columns are aesthetically beautiful too.. :)

Sir g in first Pic where the column is failing in the window there SHORT COLUMN effect is also visible ...what you think as we the length of the column is reduced due to the walls which is highly unfavorable in earthquake region because then the shear forces are high in that region and they cause such shear failure so this must also be kept in mind that the length of column is not restricted in that way that it produces short column effect......

Link to comment
Share on other sites

Sir g in first Pic where the column is failing in the window there SHORT COLUMN effect is also visible ...what you think as we the length of the column is reduced due to the walls which is highly unfavorable in earthquake region because then the shear forces are high in that region and they cause such shear failure so this must also be kept in mind that the length of column is not restricted in that way that it produces short column effect......

And sorry one more thing i like to mention here that i understand the concept which you explained to waqar i think but here it is important to tell him that such rft deatiling is very very poor for structures and he can see why it is poor .....Shear stirrups long. bars everything is not according to seismic requirements....what you say..

Link to comment
Share on other sites

And sorry one more thing i like to mention here that i understand the concept which you explained to waqar i think but here it is important to tell him that such rft deatiling is very very poor for structures and he can see why it is poor .....Shear stirrups long. bars everything is not according to seismic requirements....what you say..

Sir g in first Pic where the column is failing in the window there SHORT COLUMN effect is also visible ...what you think as we the length of the column is reduced due to the walls which is highly unfavorable in earthquake region because then the shear forces are high in that region and they cause such shear failure so this must also be kept in mind that the length of column is not restricted in that way that it produces short column effect......

Yeah, Short columns can be critical.. to summarize, "Stiffness attracts load"

Link to comment
Share on other sites

what is cracked and uncracked section analysis?????

why we use modifiers in ETABS like for beams we use 0.35 in bending and moment of inertia???what is the logic behind this?/

Something to keep in mind when using cracked section properties.

Euler Buckling Load (Pe) = pi^2 *EI / (KL)^2

In your case EI = 0.35 * Igross

This is because you are using modified stiffness parameters.

This would result in a more "critical" buckling load.

**Note: ACI doesn't usually let you get above 75% of the theoretical value .**

That's pretty typical. I don't usually see this method as being capable of predict P-Delta amplification above about 70% of the theoretical elastic buckling value.

Link to comment
Share on other sites

  • 3 weeks later...
  • Moderator

a bar in centre will be useless as rft is needed for taking tension. One can use 4 bars and use rectangular ties.

i came to know in a book that in circular column there should be six bars used in minimum also one engineer said that according to ACI code six bars are required in a load bearing circular column .

Link to comment
Share on other sites

i came to know in a book that in circular column there should be six bars used in minimum also one engineer said that according to ACI code six bars are required in a load bearing circular column .

Code does require us to use a minimum of six bars for spirals, it does not mention circular cross section in that specification. Code requires minimum of 4 bars for circular/rectangular ties.

But we can still use 4 bars in circular column as code also states, at many places, that if engineer is able to prove the safety of his design proposal in light of rules of mechanics,material behavior and serviceability requirements, than he can use it.

I answered your question keeping in mind that particular member is kind of dummy member, the one which is not an integral part of structural member.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.