Hello Guys. According to your opinion is it possible to BUILD SMRF(Special Moment Resisting Frames) in Pakistan satisfying all code requirements? Need comments of senior engineers.
There is practice among Pakistani Designers that they take value of "R" for IMRF intead of SMRF even if there building is in UBC zone 3 or 4.

Link to comment
Share on other sites

as per my understanding if we provide some additional dowel bars that are embedded in both column and beam at joint then it can resist moment. correct me if i am wrong.

Its more than that. You have to see what seismic zone your building lies and have to select the appropriate level of ductility and over-strength. I would recommend skimming through ACI Chapter 21. I have also attached some documents pertinent to the discussion that will help you develop a better understanding of aforesaid. Go through read them and if you have any question post in the forums :)

Goodluck!

How do Beam-Column Joints in RC Buildings Resist Earthquakes.pdf

How do Columns in RC Buildings Resist Earthquakes.pdf

How to make building ductile for Good Seismic Performace.pdf

How do Earthquake Affect Reinforced Concrete Buildings.pdf

What is seismic design philosophy of Buildings.pdf

Link to comment
Share on other sites

SMRF has all its provisions listed in ACI chapter 21...this is very important to read all those provisions and its serious to deal with earthquake forces....you cannot ignore a factor as with other design procedures..You have to take the appropriate values from the code. You cannot use R factor of Ordinary or intermediate frame for special frame !

Link to comment
Share on other sites

SMRF has all its provisions listed in ACI chapter 21...this is very important to read all those provisions and its serious to deal with earthquake forces....you cannot ignore a factor as with other design procedures..You have to take the appropriate values from the code. You cannot use R factor of Ordinary or intermediate frame for special frame !

Rana you are right, but i think question is related to ,"Do we have the capability to implement design requirments in the field"

Link to comment
Share on other sites

i didnt get it! what do you mean by the capability? ofcourse if you are going to build SMRF you have to build it in proper way by any means..other wise if you say you dont have the capability or resources to build it then obviously dont build it!

Link to comment
Share on other sites

i didnt get it! what do you mean by the capability? ofcourse if you are going to build SMRF you have to build it in proper way by any means..other wise if you say you dont have the capability or resources to build it then obviously dont build it!

When you do commercial design in Pakistan, not every bldg has a super construction team. Considering local practise, the best thing is to keep you seismic parameters of the zone you are in and use a lower R Value. This would be little over design but safe.

Link to comment
Share on other sites

  • 2 weeks later...

we sue R=5.5 for IMRF and R=8.5 for smrf,why we reudce the value of base shear as R is inversely proportional to the base shear as per base shear equation.

Link to comment
Share on other sites

i know the reason that increasing the R value increase the ductility of frame system..but we cant ignore the high value of base shear in zone 3 and 4..

Link to comment
Share on other sites

asad R is structural participation factor for the base shear.we make our structures in two different ways one that whole structure bears the base shear force and still remains in the elastic range there is no plastic hinge formation or non linear range... and other way is that we design our structure such that some part of base shear is resisted by structure and remaining part is shared by the ductility of the structure and structure goes into non linear range and hinges are formed.

what we prefer that our structure behave the second way so it some part remains in the elastic range and other part in plastic.Plastic hinges are only preferred in the higher zones like you mentioned 3 or 4.In low zones we don't make plastic hinges as it makes structure uneconomical so we do more elastic and little bit ductile structure.. So the value of R is kept low as this value is divided by the base shear and the force which comes out is taken by the structure and remaining is taken by the ductile part of structure....In normal zones structures are low ductile and value of R is less.

Now if we go to the higher zones like 3 or 4 what we want is that our structure should be flexible and it resist all the seismic forces and should not fail at any stage. So SMRF structure is preferred and Strong column weak beam structure is designed. So when we take value of R like 8 or 9 it means that base shear divided by R the value we get is resisted by structure and the remaining force is very big goes to the ductile part of the structure so just to get that much ductility or flexibility in the structure plastic hinge phenomena is introduced in the structure. What happens in the plastic hinge that our structure gets all the deformation and it goes to the plastic hinge region but it don't fail or fall down but this is only in very severe cases or very high zones. In plastic hinge we keep very close reinforcement at the beam column joint what happen with this reinforcement that concrete is more confined as we know that in concrete structures failure only occurs due to the cracking of concrete and steel fails at very very late stage so with this extra shear reinforcement we make structure flexible such that large deformations occur but no failure of structure.

So i hope that you will get it now and Plastic hinges are made in SMRF structures as they are specially designed to resist severe seismic actions. and plastic hinges are formed that our structure should not fail at any cost it should go in non linear range ... I suggest you to read some thing about the push over analysis and non linear hinges in structures ...

I hope that now you are much clear what i mean but still if you have any doubts please donot hesitate to ask...

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .