33 % Increase In Bearing Capacity In Transient Load Condition


Muhammad Hassan
 Share

Recommended Posts

There are 2 things..

First, the 1/3 rd stress increase for soil pressures shouldn't be taken for granted, and shall only be be used after due consultation with the geotechnical engineer. I dont have a code reference for 33% thing but if It isn't mentioned in the code, it is commonly allowed by the Geotech engineer. The following note is from the geotech report for a current project. "The net allowable bearing pressure may be increased by one-third for transient wind or seismic loads."

Second,

Another possible alternative would be to reduce forces and have a economical design ,

The 25% reduction applied to the overall overturning moment at the base of the structure due to lateral seismic forces (talking about the big picture here - not moment on an individual footing). As the structure overturning moment is generally resolved into a force couple in braced frames or individual moments in footings, I read this as allowing a reduction in either the force couple or the individual moments for design, both strength and stability, of the footings.

As basis see the 2009 NEHRP Provisions which basically provide a commentary to ASCE 7-2005 (downloadable - big file - here: http://www.fema.gov/...cord.do?id=4103) which says for this provision (emphasis added):

C12.13.4 Reduction of Foundation Overturning. Since the vertical distribution of forces prescribed for use with the

equivalent lateral force procedure is intended to envelope story shears, overturning moments are exaggerated. (See

Section C12.13.3.) Such moments will be lower where multiple modes respond, so a 25 percent reduction is permitted for

design (strength and stability) of the foundation using this procedure.

Note:This 25% reduction is for seismic only.

Edited by Umar Makhzumi
Note added
Link to comment
Share on other sites

i was making load combinations for descon new project. it was strange when i found out they are unaware of vertical component of earthquake. Except one project they don't take this. further more they are also unaware of special seismic combinations.

but one thing is encouraging tht they most deal with steel structures and when we use ASD Ev is zero. This clause has saved them till yet

Link to comment
Share on other sites

  • 1 month later...

Sir umer i had studied this document before starting discussion. This mainly adresses the stress increase in structural materials. This was practice followed before 1990's because at that time factor of 0.75 was not introduced in load combinations. We can increase allowable bearing capacity of soil by 33% under eartquake and wind conditions.

Link to comment
Share on other sites

  • Moderator

soil is the material with most unpredictable behaviour and without any strongly recommended reference it is not reasonable to increase the capacity , yes you are right!!!let the blame going to others typical approach :P

Link to comment
Share on other sites

  • 2 years later...

What I have concluded after reading above posts and documents, is that 

1) The 1/3d increase in stress by ASD method may be either due to

i) loading rate

ii) loading duration

iii) some other such reason based on engineering judgement

iV) And most importantly due the reason that when two transient loads (loads having tendency to vary in magnitude with respect to time e.g. live, earth quack, wind etc)  act simultaneously on a structure, then one transient load acts as full value load and other structure has less probability of occurrence. So it is not fair to combine these two transient loads at their full value loads. So both of the transient loads are either allowed to reduce upto some extent (As codes specify 25% reduction in transient loads) OR corresponding stress in material is increased by 33%.

 

(Note that 0.75 is reduction factor for transient simultaneously acting loads and reciprocal of 0.75 i.e. 1/0.75 = 1.33 i.e. increment factor of stress. )

 

Basic equation of equilibrium is

 

Loads = Stress 

 

In case of simultaneously acting transient loads,

 

either you can do

 

0.75*loads = stress

 

OR

 

Loads = stress/0.75 = 1.33*stress

 

But keep in mind that since this stress increment is due to the fact that both transient loads can not act simultaneously at their full value so we are reducing loads or increasing stress. This stress increment has nothing to do with DEAD LOADS. So we can not reduce dead load and this factor of 0.75 is applied only to transient loads.

 

You can find in different codes in practice two types of load combinations.

Basic and Alternate.

One type of load combinations include this 0.75 reduction factor in them so using these types of load combinations we can not increase stress. because reducing loads for the same reason and increasing stress for again the same reason SIMULTANEOUSLY is UNSAFE. You can go for one approach at a time.

 

More over, Codes also say that the effect due to load combination carrying two or more transient loads with reduced values must not be less than the effect of only one (most severe) transient load acting at full value.

Link to comment
Share on other sites

Sir umer i had studied this document before starting discussion. This mainly adresses the stress increase in structural materials. This was practice followed before 1990's because at that time factor of 0.75 was not introduced in load combinations. We can increase allowable bearing capacity of soil by 33% under eartquake and wind conditions.

The document presented by Sir Umer clearly says that this stress increment should not be taken even in case of earth quack loads if 0.75 reduction factor has been already used in load combinations.

 

More over, in sizing of footing, we go for ASD approach because bearing capacity given by geotechnical engineer is based on the concept that full factor of safety of 2-3 is applied on soil strength and no loads are increased. This is ASD methodology. So to be compatible, we also go for ASD while sizing of foundation. So in my opinion, if you are using load combinations which are carrying 0.75 reduction factor, you can not increase soil stress by 33% even not for earth quack loads. but if you are using the load combinations which are not having 0.75 reduction, then you can increase this stress as 33% but just for those cases where two or more than two transient loads are acting simultaneously.

Link to comment
Share on other sites

On 2015-02-12 at 4:29 AM, Waqas Haider said:

The document presented by Sir Umer clearly says that this stress increment should not be taken even in case of earth quack loads if 0.75 reduction factor has been already used in load combinations.

 

More over, in sizing of footing, we go for ASD approach because bearing capacity given by geotechnical engineer is based on the concept that full factor of safety of 2-3 is applied on soil strength and no loads are increased. This is ASD methodology. So to be compatible, we also go for ASD while sizing of foundation. So in my opinion, if you are using load combinations which are carrying 0.75 reduction factor, you can not increase soil stress by 33% even not for earth quack loads. but if you are using the load combinations which are not having 0.75 reduction, then you can increase this stress as 33% but just for those cases where two or more than two transient loads are acting simultaneously.

 

There are two noticeable references mentioned in this thread.

 

One is specific to Load Combinations(ASD stuff) and subsequent 1/3rd reduction, the other is about C12.13.4 of ASCE 7-05: 25% reduction of seismic overturning moment for the case of Equivalent Static Lateral Force Procedure. For some reason, all the replies have been focused on ASD Load Combinations and subsequent 1/3rd reduction. Anyways, ASD is old in a matter of few years would be completely wiped out of the scene for foundations. The current practice in industry is to use LRFD for foundation design. Moreover, make sure you touch base with the Geotechnical Engineer.  Sometimes geotech reports specify what could be done or not with regards to thread subject.

Thanks.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       